If I need a high interrupt rating I would prefer a name brand fuse from a name brand seller, but it is not often you need kA interrupt rating.
In your normal mains output you have the circuit break to handle the kA bit, it is first when you move before the circuit breaker or into industrial settings you really need kA.
And 250VAC with 0.025ohm circuit impedance is only 10kA, with normal test leads you will not even get close to this.